Anything to do with discharge lamps mercury, SON, SOX etc and their control gear! Do you just need information on how to run a lamp correctly? Post it here!
User avatar
Alex
Posts: 72
Joined: Mon Jan 13, 2025 2:10 pm
Location: Freiberg/Sachsen-Germany

Philips L4135 CWA Ballast for 180W SOX

Postby Alex » Mon Apr 27, 2026 12:44 pm

Hello,
Last meet i was given a CWA Ballast for SOX 180W by Kev of the type L4135. I got the ballast safely home and when i tried to run it, i noticed that the capacitor was mechanically brocken. I replaced it, and then tried to light my only 180W SOX lamp. It is a newer philips but is alredy used but "should" still work... Well the lamp didn't ignite, however I noticed something: The open circuit voltage is only 290V... With the lamp having an operating lamp voltage at 245V im pretty sure something is wrong...
Does anybody know the supposed open circuit voltage of that ballast?

Last week I got a Philips SRP251 180W SOX streetlight that had a proper leak transformer in it as areplacement ballast. Thatone has an open circuit voltage of around 700V which is more to my liking for these lamps. If i find the time, i plan to see if my SOX lamps works on that gear at least or if i need to hunt down a new bulb...
From Germany. Open for any trades. Especially interested in british lighting. Please ask questions!

Favorite Lamp manufacturer: GEC
User avatar
Nick217
Posts: 448
Joined: Mon Nov 09, 2015 2:31 pm

Re: Philips L4135 CWA Ballast for 180W SOX

Postby Nick217 » Mon Apr 27, 2026 6:08 pm

Ive a few I think. These a grey coloured ballast?
User avatar
Alex
Posts: 72
Joined: Mon Jan 13, 2025 2:10 pm
Location: Freiberg/Sachsen-Germany

Re: Philips L4135 CWA Ballast for 180W SOX

Postby Alex » Mon Apr 27, 2026 7:14 pm

yes
From Germany. Open for any trades. Especially interested in british lighting. Please ask questions!

Favorite Lamp manufacturer: GEC
User avatar
AngryHorse
Posts: 816
Joined: Mon Aug 03, 2015 9:56 pm
Location: Cheshire

Re: Philips L4135 CWA Ballast for 180W SOX

Postby AngryHorse » Wed Apr 29, 2026 12:39 pm

Was your replacement capacitor rated at 440 volts?
Welcome to OBLIVION
User avatar
Alex
Posts: 72
Joined: Mon Jan 13, 2025 2:10 pm
Location: Freiberg/Sachsen-Germany

Re: Philips L4135 CWA Ballast for 180W SOX

Postby Alex » Tue May 05, 2026 10:54 am

Hello,
thank you for the replies. I took the ballast out of my test bench and replaced it with the May and Christe leak transformer that can be seen in my gallery. I checked, and my SOX 180W lamps indeed works and the open circuit voltage of the may and christe is 740V. I then had againa proper look at the philips unit.
@AngryHorse, i checked and indeed ma capacitor was only rated for 380VAC so a bit short. Im am aware that this is not ideal, however it should work at least for testing--and indeed the capacitor was not the problem. The problem was a corded lead in wire into the ballast from the terminal block. I cleaned that up and retried the ballast, without lamp however and was pleased to find an open circuit voltage of 690V.
From Germany. Open for any trades. Especially interested in british lighting. Please ask questions!

Favorite Lamp manufacturer: GEC
User avatar
Nick217
Posts: 448
Joined: Mon Nov 09, 2015 2:31 pm

Re: Philips L4135 CWA Ballast for 180W SOX

Postby Nick217 » Sat May 09, 2026 7:42 am

Drop me a private message. I have over 30 of these gear sets under my stairs so can bring a few to Cornwall for you.