How many 4 x 36w Mods on a 6 amp circuit

Any sort of discussion to do with any lighting whether it be vintage to modern!
RobTDCI
Posts: 188
Joined: Sun Aug 02, 2015 10:42 am

How many 4 x 36w Mods on a 6 amp circuit

Postby RobTDCI » Thu May 04, 2017 1:21 pm

We have a problem at work where one of the lighting circuits with a 6 amp breaker keeps tripping after hours of usage. The circuit has nine, 4 x 36w magnetically ballasted mods. We have tried having fewer lit and it seems OK then and seems strange that it should start giving problems now have been in this building for 12 years. Is it possible that the circuit is slightly overloaded? It's right on the max according to my calculations including magnetic ballast losses but I don't trust my simple take on things.
User avatar
HIDLamp
Posts: 620
Joined: Sat Mar 19, 2016 9:37 pm

Re: How many 4 x 36w Mods on a 6 amp circuit

Postby HIDLamp » Thu May 04, 2017 9:38 pm

My work has 18 4x18W magnetic mods on one breaker and they seem fine (haven't examined to see what the breaker is though)
User avatar
Kev
Posts: 1015
Joined: Sat Aug 01, 2015 10:08 pm
Location: UK

Re: How many 4 x 36w Mods on a 6 amp circuit

Postby Kev » Thu May 04, 2017 11:44 pm

MCBs can weaken when used on the max over a period of time had it a good few times.
Had to change a 16A triple pole a couple months ago that was tripping on 9A when the water heater was pulling 12 per phase. Old dorman smith
User avatar
FrontSideBus
Posts: 1055
Joined: Fri Aug 07, 2015 11:04 am
Location: Liverpool

Re: How many 4 x 36w Mods on a 6 amp circuit

Postby FrontSideBus » Thu May 04, 2017 11:45 pm

Power factor correction capacitors degrading over the years and causing the circuit current to gradually rise?
Last edited by FrontSideBus on Fri May 05, 2017 9:11 am, edited 1 time in total.
User avatar
Slyspark
Posts: 3001
Joined: Mon Feb 22, 2016 11:00 pm
Location: Surrey
Contact:

Re: How many 4 x 36w Mods on a 6 amp circuit

Postby Slyspark » Thu May 04, 2017 11:59 pm

I've seen this before where a ballast is on the verge of smoking out. Kept on tripping, yet there was never anything obvious and it would just randomly do it after being on for hours. I discovered the best way to find this is to insulation test between phase and CPC at high voltage (500 or 1000V) and generally that's enough for the ballast to go into meltdown about 5 mins after you restore the power. It's one way of finding the fault I guess....

That, or as Kev has pointed out above, MCB's do sometimes just wear out, so worth replacing it, or maybe switching the MCB's over on 2 different lighting circuits and see if the fault moves with the MCB.
Bad choices make good stories!
RobTDCI
Posts: 188
Joined: Sun Aug 02, 2015 10:42 am

Re: How many 4 x 36w Mods on a 6 amp circuit

Postby RobTDCI » Fri May 05, 2017 8:14 am

Thanks for your advice guys, all good as always! ;clap

It hasn't done it sonce Wednesday, but one of the rooms affected has no Window to outside, so its a bit more of a problem than it otherwise would be. We will probably try swapping an MCB first but failing that, we will have to try and find a decent electrician, easier said than done.
User avatar
Kev
Posts: 1015
Joined: Sat Aug 01, 2015 10:08 pm
Location: UK

Re: How many 4 x 36w Mods on a 6 amp circuit

Postby Kev » Fri May 05, 2017 12:41 pm

Or even easier you would most likely be fine to bang a 10A in there